Rupture Disc Nozzle Location

Rupture Disc Nozzle Location

Rupture Disc Nozzle Location

(OP)
Usually the nozzle for a rupture disc on a water cooled high pressure gas T&S heat exchanger is located at the top of the shell.

Is it acceptable to locate the nozzle at the bottom of the shell from a safety point of view?

Thanks
Replies continue below

Recommended for you

RE: Rupture Disc Nozzle Location

The reason I thought nozzles are typically placed on top of the equipment is so that fouling materials or solid objects cannot settle in the nozzle thus blocking the safety relief path.

RE: Rupture Disc Nozzle Location

Stampe
The relief needs to be on the top.  The point of the relief is to let gas exit the exchanger.  If you put it on the bottom all the liquid will have to drain out before the gas can escape.  You would then have to size the relief for a liquid relieving rate.
Pkpbip makes some good points about plugging as well.


Good Luck

StoneCold

RE: Rupture Disc Nozzle Location

What is the shell fluid ?

RE: Rupture Disc Nozzle Location

(OP)
Liquid drain out was my main concern with respect to safety especially due to potential pressure built-up on the shell side, but also due to high velocity liquids in the flare system.

The case is that a vendor has supplied this to us on a 250 barg compressor CM after cooler and I just wanted to make sure that this was not common practice.

RE: Rupture Disc Nozzle Location

What about protecting the cooling water system from gas penetration and pressure buid up, with probable hammering and even cooling tower "problems" ?  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close