Hi,
I need help in design of a 1000 sqft Yoga room. This will be a zone by itself in a building. May want to go up to about 90-deg-F, in summer. I can put in a stand-alone system for this area. Any ideas?
Thanks,
Use a radiant floor heating system- either electric or if the building has a boiler/hot water hydronic system, use that. If the room is hoing to have a new floor put in, then installing in-floor heat would be best for the yoga folks.
The yoga style requiring this elevated temperature is the Bikram style- the work area need to be at 85 - 100 F.
I would suggest either under floor heating or reverse cycle air-conditioning.
Thank you Guys for your ideas. This building can only have equipment on the roof. No hydronics is connected to this building. One rep is telling me that a normal DX rooftop in heating mode can not bring the space temp up to 90-F. Is this correct? How hight can a DX unit in heating mode go, and does it matter if it ia gas heat or electric heat? Is there a specialty unit for this sort of applications?
thanks,
OK, electric floor radiant heat is your practical choice- you cannot do this with an air system. Yoga is a floor activity. Look at the NuHeat product (
) or do a google search for electric radiant floor heating and see what might be locally supplied. It's not usually a big amperage or power draw, and would be less electrical power than a new AHU. Then you can maintain the 90F-100F "resultant" or "operative" temperature without huge hot air inputs. Mean radiant temperature is just as, or more important than simply "air temperature".