glory102
- Jun 24, 2011
- 3
Hey,
I have two mobile delta-wye transformers that I need to find the X/R ratio for. The following is the information I have on each transformer:
Transformer 1:
72KV/25.05KV
25MVA
Load Losses: 316.8 KW (@ 25MVA)
Z%: 16.4
Transformer 2:
138KV/24.94KV
25MVA
Load Losses: 327.5 (@ 25MVA)
Z%: 18.0
I have done some research into finding the ratio, but when I try the method with a Transformer where I know the X/R ratio its off. The method I was trying was:
%R = Load Losses/25MVA, %X = SQRT(%Z^2 - %R^2), %X/%R.
With this method I get the following:
Transformer 1 - X/R = 12.903
Transformer 2 - X/R = 13.7
Any help is greatly appreciated,
Thanks.