We have one MCC-fed compressor motor application where motor uses an open-transition wye-delta start. It is the only application in the plant with wye-delta start. Don’t ask me why we have it... I know of no good reason.
We measured 40 millisecond dead time between open of the wye and close of the delta. And we saw a current spike that occurs upon transition from wye to delta as result of out-of-phase condition of motor residual voltage and incoming voltage as expected. Even if motor speed didn’t change, there is phase difference between delta and wye connections.
We have experienced intermittent tripping of the molded case circuit breaker. I don’t know details of the settings. I was asked to provide general input/reference about the setting of molded case circuit breaker instantaneous for this type of application.
My questions (in order of importance):
1. What guidance is available for selecting molded case circuit breaker instantaneous setpoint (other than obvious coordination requirements with upstream devices and protection of cables).
2. NEC gives suggested mcb instantaneous settings as multiple of FLA, are these applicable to wye-delta start?
3. Any rough idea of how much variability in spike upon starting to delta from one start to the next (we have measured the current spike once, not sure how representative it is)
4. Is there a means to predict the worst-case current spike?
5. Is there any logical reason to have a wye-delta start in a power plant ?
Thanks in advance for any insight.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
We measured 40 millisecond dead time between open of the wye and close of the delta. And we saw a current spike that occurs upon transition from wye to delta as result of out-of-phase condition of motor residual voltage and incoming voltage as expected. Even if motor speed didn’t change, there is phase difference between delta and wye connections.
We have experienced intermittent tripping of the molded case circuit breaker. I don’t know details of the settings. I was asked to provide general input/reference about the setting of molded case circuit breaker instantaneous for this type of application.
My questions (in order of importance):
1. What guidance is available for selecting molded case circuit breaker instantaneous setpoint (other than obvious coordination requirements with upstream devices and protection of cables).
2. NEC gives suggested mcb instantaneous settings as multiple of FLA, are these applicable to wye-delta start?
3. Any rough idea of how much variability in spike upon starting to delta from one start to the next (we have measured the current spike once, not sure how representative it is)
4. Is there a means to predict the worst-case current spike?
5. Is there any logical reason to have a wye-delta start in a power plant ?
Thanks in advance for any insight.
=====================================