dik
Structural
- Apr 13, 2001
- 26,063
We have a project where the contractor has used the wrong voidform under a slab.
Two types of plastic foam voidform were specified, one for gradebeams and one for the slab. Voidform for gradebeams has a higher 'crushing' strength than that for the slab.
The contractor erroneously used the gradebeam void under the slab. Two slab areas are involved. One, well within the building plan and the other on a corner of the building.
Soils in this area are highly plastic (swelling with moisture) clays.
My initial thoughts are that it is unlikely that the interior one will be a problem. Experience is that the soil within a building dessicates and that the soil shrinks away from the void anyway. This same dessication occurs around the perimeter to some extent with the dryer soil tending to remove moisture from the perimeter soil.
There are no pipes within the void space that can leak.
I'm of the opinion that it is OK to live with the situation and that uplift damage is unlikely (not impossible <G>). Repair is difficult and costly to the contractor.
I can stress that the perimeter drainage in the corner area must be 'flawless' in operation to eliminate perimeter moisture.
I can check the slab (which is reinforced both top and bottom continuously) to determine what amount of uplift the slab can accommodate; this detracts from my argument that the soil will shrink away from the slab.
Does anyone have information on the dessication of soil within a building or other suggestions? Using a Tiger Torch to melt the void would not likely be a good idea.
Dik
Two types of plastic foam voidform were specified, one for gradebeams and one for the slab. Voidform for gradebeams has a higher 'crushing' strength than that for the slab.
The contractor erroneously used the gradebeam void under the slab. Two slab areas are involved. One, well within the building plan and the other on a corner of the building.
Soils in this area are highly plastic (swelling with moisture) clays.
My initial thoughts are that it is unlikely that the interior one will be a problem. Experience is that the soil within a building dessicates and that the soil shrinks away from the void anyway. This same dessication occurs around the perimeter to some extent with the dryer soil tending to remove moisture from the perimeter soil.
There are no pipes within the void space that can leak.
I'm of the opinion that it is OK to live with the situation and that uplift damage is unlikely (not impossible <G>). Repair is difficult and costly to the contractor.
I can stress that the perimeter drainage in the corner area must be 'flawless' in operation to eliminate perimeter moisture.
I can check the slab (which is reinforced both top and bottom continuously) to determine what amount of uplift the slab can accommodate; this detracts from my argument that the soil will shrink away from the slab.
Does anyone have information on the dessication of soil within a building or other suggestions? Using a Tiger Torch to melt the void would not likely be a good idea.
Dik