Dear Gentelmen:
I am the going to take part of a start up of a big Wound Rotor Motor and this is my first time with 700HP motor).
I will appreciate so much if anybody of you can give me some values according to a similar experience and application. What I really need is the time of every timer that will eliminate every step of the resistor.
t1= ??sec (will eliminate R1-R2, see data below)
t2= ??sec (will eliminate R2-R3, see data below)
t3= ??sec (will eliminate R3-R4, see data below)
t4= ??sec (will eliminate R4-R5, see data below)
t5= ??sec (will eliminate R5-R6, see data below)
RESISTOR
R1-R2 .73 ohms, 142.8 amps
R2-R3 .40 ohms, 163.2 amps
R3-R4 .24 ohms, 204 amps
R4-R5 .16 ohms, 224.4 amps
R5-R6 .08 ohms, 244.8 amps
700 HP – WOUND ROTOR MOTOR
FS: 1.15
Duty: continuous
Manufacturing Standard: NEMA
Voltage Stator: 4160V,
Current: 106.6A.
Voltage Rotor: 1140V
Current Rotor: 272 A.
Rated frequency: 60 HZ
Start Torque: 180%
Max. Torque: 250%
Starter per hour: 3
Load: Crusher.
The load is a very critical part of the facility.
Thank you in advance for your valuable support.
Daniel
I am the going to take part of a start up of a big Wound Rotor Motor and this is my first time with 700HP motor).
I will appreciate so much if anybody of you can give me some values according to a similar experience and application. What I really need is the time of every timer that will eliminate every step of the resistor.
t1= ??sec (will eliminate R1-R2, see data below)
t2= ??sec (will eliminate R2-R3, see data below)
t3= ??sec (will eliminate R3-R4, see data below)
t4= ??sec (will eliminate R4-R5, see data below)
t5= ??sec (will eliminate R5-R6, see data below)
RESISTOR
R1-R2 .73 ohms, 142.8 amps
R2-R3 .40 ohms, 163.2 amps
R3-R4 .24 ohms, 204 amps
R4-R5 .16 ohms, 224.4 amps
R5-R6 .08 ohms, 244.8 amps
700 HP – WOUND ROTOR MOTOR
FS: 1.15
Duty: continuous
Manufacturing Standard: NEMA
Voltage Stator: 4160V,
Current: 106.6A.
Voltage Rotor: 1140V
Current Rotor: 272 A.
Rated frequency: 60 HZ
Start Torque: 180%
Max. Torque: 250%
Starter per hour: 3
Load: Crusher.
The load is a very critical part of the facility.
Thank you in advance for your valuable support.