The duration of load is based on how long the load is applied to the member, connections, etc. over the life of the members. This loading is cumulative over the life of the member. Assuming that the handrail is not replaced for ten years. I see the possibility of the 200 lb load being applied (10, 20, 30 seconds at a time) for more than the ten minutes allowed for by the 1.6 increase at some locations along the handrails. For this reason (when the use of the 1.0 factor was a problem) the maximum I would ever want to use is 1.25, a seven day duration factor.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.