I need to make connection to equipment with flying leads (special high temp wires rated for 150 deg.C ampacity).If I need to use NEC 75 deg.C rated wires connected to that equipment, what would be the best way to reduce temperature to 75C level? May be use a piece of copper bar between those two wires and trying to estimate the temperature gradient (decline) along the bar length? Please advise.
 
Replies continue below

Recommended for you

I'm confused. Supposedly the 150C wire is rated so high because it needs to carry a lot of current at a lower-than-normal gauge for a certain distance. At some point, however, it has to attach to wire of some other gauge... so what would the bus bar gain you? Make the attachment wire of a thicker gauge, allowing it to carry the same current but at 75C.

Dan - Owner
Footwell%20Animation%20Tiny.gif
 
Thanks for reply, Dan. A bit more details. Under normal operating conditions, these 150C wires are terminated to the equipment also rated for 150C operations. We need to test a part of this system, so we need a transition to lower temp rated wires. The question is about temperature rating of the termination point. I do not beleive I can connect at one point (say, stud) the 150C running hot wire, and a larger size (for the same ampacity) 75C rated wire(or wires.
 
??? If you're running this to equipment not rated for 150ºC, then the 150ºC rated wires MUST at some point in time drop in temperature. I would think that a couple of feet of wire outside of the 150ºC environment would be enough to drop down the wire temperature to the desired level.

TTFN

FAQ731-376
Chinese prisoner wins Nobel Peace Prize
 
What IR said... just because the wire is rated for 150C doesn't mean it runs at that temp the entire way. I mistakenly was under the impression the wire would get up to 150C due to a smaller than typical gauge... now I realize it's the insulation's rating. At some point outside of the equipment the wire will be subject to more normal temps.