Jeremiah187
Mechanical
- Mar 14, 2008
- 22
Gents,
I posed a question over a year ago with regards to window sprinklers. Just want to clarify.
If you use Tyco WS "closed" window sprinklers do they need to be on their own zone?
Was putting window sprinklers on their own zone only due to the older "open type" heads?
Application is interior stairwell wall, glazing makes part of the fire rating. Arch. will not do the fire rated glass.
Cheers,
Jeremiah
I posed a question over a year ago with regards to window sprinklers. Just want to clarify.
If you use Tyco WS "closed" window sprinklers do they need to be on their own zone?
Was putting window sprinklers on their own zone only due to the older "open type" heads?
Application is interior stairwell wall, glazing makes part of the fire rating. Arch. will not do the fire rated glass.
Cheers,
Jeremiah