AusLee
Electrical
- Sep 22, 2004
- 259
Hi,
I'm Electrical so forgive the question if too dumb.
I'm working on a residential project where some apartment windows need to be drenched to avoid the risk of fire coming inside the unit from a source adjacent to the unit (the building has a funny architecture).
Now a question is coming up: what if the windows are open in case of fire?
The windows are motorized and there is a provision for a relay connected to the fire panel to trigger the window close mechanism. But the concern is that power to the apartment is not a Safety service and the apartment may lose power in case of fire (the incoming cables not being fire rated).
So there is talk that these windows be supplied from a safety service using fire rated cables and with back-up power source.
But the problem is, not all windows in all buildings are motorized as we all know.
Q1: So what happens in the case of buildings that have manual operated windows? surely no one expects that all windows will be closed in case of a fire in such buildings: what if someone was away from home and had left the window open?
Q2: Has motorization been specifically requested in this project for the purpose of making sure the windows will close, but the original design has fallen short from specifying the back-up power supply? Note for example that not all buildings have back-up generators so buildings with lifts required to operate in emergency mode might still find it that in case power is lost to the building, these emergency lifts will also be out of service? Emergency lighting and sprinkler pumps do have prescribed back-up power requirements in residential buildings but not the lifts, so what about these windows, any code requirement for their power supply?
In my mind I think there is no issue in the windows being open, the worst case is that water will come inside the apartment and wet everything; the flow of water calculated as per the standard will also be sufficient to fight the incoming flame (so many liters per square meter).
If you could please shed some light on this issue, all my searches led to see how the sprinkler is installed but nothing about the status of the window.
Thanks
I'm Electrical so forgive the question if too dumb.
I'm working on a residential project where some apartment windows need to be drenched to avoid the risk of fire coming inside the unit from a source adjacent to the unit (the building has a funny architecture).
Now a question is coming up: what if the windows are open in case of fire?
The windows are motorized and there is a provision for a relay connected to the fire panel to trigger the window close mechanism. But the concern is that power to the apartment is not a Safety service and the apartment may lose power in case of fire (the incoming cables not being fire rated).
So there is talk that these windows be supplied from a safety service using fire rated cables and with back-up power source.
But the problem is, not all windows in all buildings are motorized as we all know.
Q1: So what happens in the case of buildings that have manual operated windows? surely no one expects that all windows will be closed in case of a fire in such buildings: what if someone was away from home and had left the window open?
Q2: Has motorization been specifically requested in this project for the purpose of making sure the windows will close, but the original design has fallen short from specifying the back-up power supply? Note for example that not all buildings have back-up generators so buildings with lifts required to operate in emergency mode might still find it that in case power is lost to the building, these emergency lifts will also be out of service? Emergency lighting and sprinkler pumps do have prescribed back-up power requirements in residential buildings but not the lifts, so what about these windows, any code requirement for their power supply?
In my mind I think there is no issue in the windows being open, the worst case is that water will come inside the apartment and wet everything; the flow of water calculated as per the standard will also be sufficient to fight the incoming flame (so many liters per square meter).
If you could please shed some light on this issue, all my searches led to see how the sprinkler is installed but nothing about the status of the window.
Thanks