setiawanmarten
Electrical
- Aug 17, 2011
- 13
Dear all,
We just test transfomer 3000 KVA , primer 20.000 V and secunder 90 V.
We test the winding insulation resistance :
P to ground (with secunder Short to Ground) result : 13.200 MegOhm
S to ground (with primer short to ground) result : 2000 MegOhm
Primer to secunder was 191 Meg Ohm,
The minimum insulation resistance according to IEEE C57.125 (EASA AR200 section 2 page 2) for primer to ground we use the primer voltage for the formula(E),
For secunder to ground we use secunder voltage to the formula (E),
My question if we already measure winding insullation resistance P to Ground (secunder short to ground) and winding insulation resistance S to ground ( primer short to ground) do we have to also measure the value of winding insulation resistance of Primer to secunder? And if we have to measure then what is formula for the minimum value of primer to ground ( i mean for the E value, which voltage do i have to put to the formula? Secunder or primer? )
Thank you
We just test transfomer 3000 KVA , primer 20.000 V and secunder 90 V.
We test the winding insulation resistance :
P to ground (with secunder Short to Ground) result : 13.200 MegOhm
S to ground (with primer short to ground) result : 2000 MegOhm
Primer to secunder was 191 Meg Ohm,
The minimum insulation resistance according to IEEE C57.125 (EASA AR200 section 2 page 2) for primer to ground we use the primer voltage for the formula(E),
For secunder to ground we use secunder voltage to the formula (E),
My question if we already measure winding insullation resistance P to Ground (secunder short to ground) and winding insulation resistance S to ground ( primer short to ground) do we have to also measure the value of winding insulation resistance of Primer to secunder? And if we have to measure then what is formula for the minimum value of primer to ground ( i mean for the E value, which voltage do i have to put to the formula? Secunder or primer? )
Thank you