Windfarm Collection System & Grounding.

Status
Not open for further replies.

BJC

Electrical
Jan 29, 2001
2,119
I am reviewing a wind farm collection system.
The system is radial with up to 7 generators on one radial. The transformers are Y-D 600 volt delta -up to 34.5 kV. The tranformer terminals on the MV side are 600 amp feed thru, with dead break elbows.
The 34.5 side has a D-Y grounding transformer (X-0 grounded).
My question is: Is this normal?
I would have used single feed tranfromer with a combination 600 and 200 amp dead break elbow connectors. That way one generator/transformer doesn't take out all or most of a radial.
The only good way to detect a 34.5 kV system ground is at the collection substation. The low side breakers on each generator stup up transformer are shut tripped from the radial PCB.

I would recommend directional fault indicators on all radial collectors. Clearing a ground fault would be a long process without them.
Your thoughs and comments please.
Thank You
 
Replies continue below

Recommended for you

Typical cheap wind farm system. They don't ask how to do it well, they ask how to do it cheap.
 