lsmfse
Structural
- Nov 19, 2001
- 147
I am designing a concrete top for a roadway box. The span is 6'. I am designing the slab based on a 1'-0" strip. Based on my research, AASHTO(1992 edition) gives a distribution width of 4+.06S.(Reinforcement paralell to traffic) This gives 4.36', therefore, I assume that for a 16k wheel load, I would have 16/4.36 or 3.67k/ft(not including impact)and a moment of 3.67x6/4= 5.51 ft-k. In the same section, moments may be approximated as 900S which in my case would = 5.4 ft-k. Could someone confirm my interpetation? I remember years ago my superiors would use a number of 12"+2x slab thickness(something like this)for concentrated loads on floors. If I applied this "rule of thumb", my moment is on the order of 11.08 ft-k, almost double.
Thanks
Thanks