What is the general practice of grounding the sheath of control cables especially in HV substation/ switch yard. Do you ground the sheath or screen of the cable only at one end or at both the sends of the control cable?
 
One end.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Agreed; one end ONLY so as to preclude circulating currents.

This thread ONLY to be used going forward; I have asked for your double post in EP&T&D forum be deleted, as double posting is forbidden.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
In HV substations, control cable sheaths are typically grounded at one end, known as single-point grounding. This minimizes circulating currents and provides a reference point for the control system. Double-point grounding may be used in specific cases, but adherence to manufacturer recommendations and system design considerations is crucial.

 