Apr 5, 2004 #1 Warpspeed Automotive Joined Jun 6, 2003 Messages 1,521 Location AU I have a single phase 240v 50Hz Brinsmead condenser fan motor rated at 0.28 Hp, 1.45 full load amps. It is the usual two winding capacitor start/run type motor. What value of capacitance would usually be used with something like this ?
I have a single phase 240v 50Hz Brinsmead condenser fan motor rated at 0.28 Hp, 1.45 full load amps. It is the usual two winding capacitor start/run type motor. What value of capacitance would usually be used with something like this ?
Apr 5, 2004 #2 imok2 Mechanical Joined Oct 21, 2003 Messages 1,311 Location US Startreck: For a 60 hz 240 volt 1/4 HP it would be 5mfd at 370 volts. I don't know it would be OK at 50hz Roger Upvote 0 Downvote
Startreck: For a 60 hz 240 volt 1/4 HP it would be 5mfd at 370 volts. I don't know it would be OK at 50hz Roger
Apr 5, 2004 Thread starter #3 Warpspeed Automotive Joined Jun 6, 2003 Messages 1,521 Location AU Thank you Roger, I will give it a try. Upvote 0 Downvote