Once you include the final zero in 2750 MVA, it is just Amps x Volts x 1.732 x 25.
A rating of 4292 amps seems really big for internal fuses. Although there is a type of pole mounted transformer called Completely Self Protected (CSP), the CPS transformers max out around 167 kVA.
I had assumed self protecting was simply a redundant way of indicating no external impedance was needed at low fault levels. IEEE C57.12.00 list various withstand requirements for various categories of transformers. Note that there is also a maximum duration of fault the transformer is designed to withstand.