Bestboy
Electrical
- Jan 11, 2006
- 23
I am doing a motor control upgrade.
The present installation is as follows:-
· 400V, 15 KW, 2pole, 3Ph sq-cage induction motor spinning a high inertia fan.
· Cable from sub-station isolating fuses to the starter and then the motor 6mm sq – a distance of 18 meters
· Fuse rating 80 A
· Starter – direct on line
The new installation will consist of:-
· A similar motor as above but 18.5kW
· 18.8kW VSD
The VSD installation manual specifies that I should use:-
· 60A eternal fuses
· 100A circuit breaker
· Cable size 14mm sq (6 AWG) R,S,T and 8mm sq (8 AWG) U,V,W
This cable sizes do not make sense to me. I am planning to use 16mm sq PVC armoured cable from the substation to the VSD on a cable tray – a distance of 10 meters and 10mm sq from the VSD to the motor a distance of 8 meters.
I am thinking of de-rating the fuses to 60A and use a 100A circuit breaker in VSD panel. Some one else suggested to me to leave the 80A fuses as they are.
Any comment? Assistance much appreciated. Thanking you in advance
The present installation is as follows:-
· 400V, 15 KW, 2pole, 3Ph sq-cage induction motor spinning a high inertia fan.
· Cable from sub-station isolating fuses to the starter and then the motor 6mm sq – a distance of 18 meters
· Fuse rating 80 A
· Starter – direct on line
The new installation will consist of:-
· A similar motor as above but 18.5kW
· 18.8kW VSD
The VSD installation manual specifies that I should use:-
· 60A eternal fuses
· 100A circuit breaker
· Cable size 14mm sq (6 AWG) R,S,T and 8mm sq (8 AWG) U,V,W
This cable sizes do not make sense to me. I am planning to use 16mm sq PVC armoured cable from the substation to the VSD on a cable tray – a distance of 10 meters and 10mm sq from the VSD to the motor a distance of 8 meters.
I am thinking of de-rating the fuses to 60A and use a 100A circuit breaker in VSD panel. Some one else suggested to me to leave the 80A fuses as they are.
Any comment? Assistance much appreciated. Thanking you in advance