A contractor damaged a r/c retaining wall and had to have to wall demolished and repaired. In order to save time he cut the rebard but cut it about 1 foot above the footing and as such the required lap lenghts can no longer be satisfied. I've already checked As provided versus As required.
The contractor has proposed welding using a 6013 electrode which has a yield strength of 410MPa (60,000 psi) but I am a bit weary since where I am located welders don't go through any formal training and certianly they don't practice to AWS. The rebar is 400 MPa steel. From my readings he needs to use an electrode with a yield atleast 550 MPa (80,000 psi) and there are other issues regarding the carbon and Manganese content of the rebar.
I know this may sound weird but is it possible to ask the contractor to provide standard hooks for both the steel that is sticking out the footing and the new steel that is being placed to reduce the development length?
Alternatively I can have him drill and epoxy dowel into the footing.
Any thoughts? Thanks.
A contractor damaged a r/c retaining wall and had to have to wall demolished and repaired. In order to save time he cut the rebard but cut it about 1 foot above the footing and as such the required lap lenghts can no longer be satisfied. I've already checked As provided versus As required.
The contractor has proposed welding using a 6013 electrode which has a yield strength of 410MPa (60,000 psi) but I am a bit weary since where I am located welders don't go through any formal training and certianly they don't practice to AWS. The rebar is 400 MPa steel. From my readings he needs to use an electrode with a yield atleast 550 MPa (80,000 psi) and there are other issues regarding the carbon and Manganese content of the rebar.
I know this may sound weird but is it possible to ask the contractor to provide standard hooks for both the steel that is sticking out the footing and the new steel that is being placed to reduce the development length?
Alternatively I can have him drill and epoxy dowel into the footing.
Any thoughts? Thanks.