Consider a bent plate pole section, 16 sides, 36" in diameter.
Pole plate is 1/2" wall
Base plate is 2" thick
Pole and base plate are A572-50ksi
Welded joint is similar to TC-U4a-GF (AWS prequalified CJP, GMAW)
Application is telecom / utility pole, where wind governs (TIA 222-G and ASCE 7-05 are governing codes)
Cyclic vs. non-cyclic: for some reason, TIA 222-G does not address whether poles and towers should be considered static structure or cyclically loaded structures, even thought the testing and detailing requirements are quite different. I believe most design-build fabricators treat these structures as statically loaded for purposes of AWS requirements.
1. Is it acceptable to use ASTM A36 (36 ksi) backer. Backer is permanent (left in place).
2. Does the AWS code require NDT? It appears like the AWS code leaves NDT completely up to engineer - correct? Seems like visual inspection + UT is appropriate, even if "static" structure.
Pole plate is 1/2" wall
Base plate is 2" thick
Pole and base plate are A572-50ksi
Welded joint is similar to TC-U4a-GF (AWS prequalified CJP, GMAW)
Application is telecom / utility pole, where wind governs (TIA 222-G and ASCE 7-05 are governing codes)
Cyclic vs. non-cyclic: for some reason, TIA 222-G does not address whether poles and towers should be considered static structure or cyclically loaded structures, even thought the testing and detailing requirements are quite different. I believe most design-build fabricators treat these structures as statically loaded for purposes of AWS requirements.
1. Is it acceptable to use ASTM A36 (36 ksi) backer. Backer is permanent (left in place).
2. Does the AWS code require NDT? It appears like the AWS code leaves NDT completely up to engineer - correct? Seems like visual inspection + UT is appropriate, even if "static" structure.