It is worth noting that the VFD used is an AFE (active front end) and they operate on a higher DC link voltage than a 'standard' 6 pulse rectifier pwm drive. This means the output peak-peak voltage will be somewhat higher than normal, I'm not sure of the exact figure but around 10-15% higher.
Normally, this would not pose too much an issue on a cable length of 30m and the fact yorgi has advised that there is also a dv/dt filter fitted but if there was some problem with the WEG motor to start, there is a possibility the higher p-p volts could find out this weakness quickly.
Yorgi, your opening question related to how others see WEG motors regarding reliability. I think the responses from most highlight a similar theme that 'generally' the product is ok but as this post has developed then it is clear that the issue is quite different and it seems that the local service and support is very questionable. This is a different issue but probably more important; you can have the best product in the world but if the local support is poor it will mean this will always be the common denominator.