I have a situation where I am reviewing a set of PEMB drawings for a building that was purchased and delivered over 10 years ago. The owner at the time elected to not erect the building, but new owners would like to put the building up. The original PEMB supplier went out of business so we are in the process of verifying that the drawings conform to current code requirements. This is actually a pretty simple building because there are no web tapered members so it makes the verification process much less rigorous.
The structure is a simple frame that is an addition to a larger building and is in SDC A. The roof is a single slope and we have designed the existing building to connect to the addition so that there is no differential deflections between the two frames. All members check out structurally, however the columns do not have sufficient web strength to resist panel zone shear effects because there is only moment acting on one side of the column. The connection of the rafter is a flush end plate on top with an unstiffened extension on the bottom. Moments induced by gravity are significantly higher than moments induced by lateral loads. The provided web thickness is 3/16" and the required thickness is 5/16" so I am designing diagonal web stiffeners to strengthen the web zone. This is about the only option as transverse stiffeners are already in place at the beam flange locations, so a web doubler is probably not a viable option.
I find it hard to believe that this connection is as under-designed as it is because loading of the structure went down under new code requirements (old code 30 psf SL; new code 23 psf SL). I am trying to figure out how this connection could have been designed originally (I know that most PEMB designers use some form of black magic to make their buildings work
so I can determine if I am making an incorrect assumption in the capacity of the connection.
While reviewing AISC J.10-6 there is a statement that "When frame stability, including plastic panel-zone deformation, is considered in the analysis;. Using this statement increases the capacity of the connection. What does this statement actually mean? Would this be a situation where for seismic purposes a frame was designed so that the beam would have a plastic hinge type failure near the connection? If that is not the case, how would one go about determining if a plastic panel-zone deformation was considered in the design? For this case, assuming that plastic panel-zone deformation had been included only gets me a 15% increase so column web stiffening would still be required. I would just like to better understand the intent of AISC requirements.
The structure is a simple frame that is an addition to a larger building and is in SDC A. The roof is a single slope and we have designed the existing building to connect to the addition so that there is no differential deflections between the two frames. All members check out structurally, however the columns do not have sufficient web strength to resist panel zone shear effects because there is only moment acting on one side of the column. The connection of the rafter is a flush end plate on top with an unstiffened extension on the bottom. Moments induced by gravity are significantly higher than moments induced by lateral loads. The provided web thickness is 3/16" and the required thickness is 5/16" so I am designing diagonal web stiffeners to strengthen the web zone. This is about the only option as transverse stiffeners are already in place at the beam flange locations, so a web doubler is probably not a viable option.
I find it hard to believe that this connection is as under-designed as it is because loading of the structure went down under new code requirements (old code 30 psf SL; new code 23 psf SL). I am trying to figure out how this connection could have been designed originally (I know that most PEMB designers use some form of black magic to make their buildings work

While reviewing AISC J.10-6 there is a statement that "When frame stability, including plastic panel-zone deformation, is considered in the analysis;. Using this statement increases the capacity of the connection. What does this statement actually mean? Would this be a situation where for seismic purposes a frame was designed so that the beam would have a plastic hinge type failure near the connection? If that is not the case, how would one go about determining if a plastic panel-zone deformation was considered in the design? For this case, assuming that plastic panel-zone deformation had been included only gets me a 15% increase so column web stiffening would still be required. I would just like to better understand the intent of AISC requirements.