Web Crippling on Elevated Composite steel deck

Status
Not open for further replies.

dylansdad

Structural
Nov 15, 2005
134
I am proposing to support a rather large (Pu=6k) load on an elevated composite deck system.
The load will be applied through a 4"x4" sq. plate.
There will be post shoring installed beneath the applied loads
The allowable phi*Rb for this deck (4" bearing) is 1220 lb/ft.
My question is, should web crippling be a concern?
Thanks in advance for any advice.
 
 http://files.engineering.com/getfile.aspx?folder=8392f605-998a-402f-a76d-663473ea1a04&file=composite_slabl.pdf
Replies continue below

Recommended for you

If your load is right over your shoring then I don't think that crippling is a concern. I'd investigate the concrete's ability to transfer load through the floor deck in its own.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Thanks for the reply. We would anticipate (design) the shoring to be directly below the applied loads.
 