I am looking for some assistance on slab / foundation joints for use in a water tank.
The tank wall has 12” cast-in-place concrete walls with an ID of 30’. I currently show a thickened continuous ftg that is 6’-6” wide x 1’-0” thk transitioning at a 3H to 1 V slope to a 6” slab (all poured at the same time). The slab is reinforced with #5’s @ 12” oc EW. I currently show (2) tooled/saw cut joints running each direction at 15’-0” apart. I show the rebar running thru the joint with a cast-in waterstop.
It seems like there are varying details…
- To run the rebar through the joint, to stop all of the rebar short of the joint, or to run half of the rebar through the joint
- Some don’t provide a waterstop, but it seems like ACI 350 is pretty clear that it is required
- It seems like a good idea to provide a joint at the thin point of the ftg to slab transition, but that would be a circular joint. I’m not sure that the specified waterstop can bend at that radius or how easy that will be to cut/tool in.
- Because the slab meets the min. reinforcing of ACI 350 for joints at 37'-6" (max diameter including the footing), does that mean that no joints are required as there is enough steel to hold the cracks tight? Any opportunity to skip joints seems like a good choice as those are typically the problem areas.
- Is there a better alternative altogether? All of my previous tanks were much larger (105’ ID) and used a post-tensioned slab with no joints. Because this tank is so much smaller, it didn’t seem worth going to post-tensioning.
The tank wall has 12” cast-in-place concrete walls with an ID of 30’. I currently show a thickened continuous ftg that is 6’-6” wide x 1’-0” thk transitioning at a 3H to 1 V slope to a 6” slab (all poured at the same time). The slab is reinforced with #5’s @ 12” oc EW. I currently show (2) tooled/saw cut joints running each direction at 15’-0” apart. I show the rebar running thru the joint with a cast-in waterstop.
It seems like there are varying details…
- To run the rebar through the joint, to stop all of the rebar short of the joint, or to run half of the rebar through the joint
- Some don’t provide a waterstop, but it seems like ACI 350 is pretty clear that it is required
- It seems like a good idea to provide a joint at the thin point of the ftg to slab transition, but that would be a circular joint. I’m not sure that the specified waterstop can bend at that radius or how easy that will be to cut/tool in.
- Because the slab meets the min. reinforcing of ACI 350 for joints at 37'-6" (max diameter including the footing), does that mean that no joints are required as there is enough steel to hold the cracks tight? Any opportunity to skip joints seems like a good choice as those are typically the problem areas.
- Is there a better alternative altogether? All of my previous tanks were much larger (105’ ID) and used a post-tensioned slab with no joints. Because this tank is so much smaller, it didn’t seem worth going to post-tensioning.