invent11
Mechanical
- Sep 10, 2007
- 47
Having ordered a 60g Elec. Water Heater for an industrial facility to be installed on a domestic water system, now noticed that WH P&T pressure setting is 150 psig whereas my system design pressure per flow diagram is 100 psig. WH vendor is not ready to change the RV to one w/ 100 psig set pressure. To resolve the issue i am thinking to install one RV on piping right downstream the WH w/ 100 psig set pressure. I am wondering do i need another RV w/ the same 100 psig setting upstream the WH and on cold water supply or the one on hot water line is adequate?
Thank you for your input. Next time i am adding an equipment to any system i check its Flow Diagram/sheet carefully!