Hi any guru,
We need to supply load that Nominal load only 32 A.
Tthere is Main Juntion Box(3 phase)that will distribute to 3 Sub Juntion Box(each phase.
Base on Cable Datasheet;
4C-6 sq.mm. can carrying 61A.
2C-10 sq.mm. can carrying 81A.
If I used cable incomer for main junction box(3 Phase)- 4C-6 Sqmm lenght 30 m.(the reason we don't use 4C-10 sq.mm because material shortage)
,and sub Junction box (1 Phase)outgoing - 2C-10 Sq.mm lenght 90 m.
From calculation,
VD main JB - 0.5%
VD Sub JB - 1.5% (If we used 2C-6 Sq.mm VD will more than 1.5%)
So,Total VD -2 % will meet our specification.
My concern is that looks funny because cable sizing sub JB (2C-10) bigger than MainJB(4C-6 sq.mm).
Above solution is possible way or able to use or not ???
Thanks for any answer