How do you proceed with the voltage drop calculation of a circuit that has various conductor sizes, material, lengths and 1 vs 2 conductors per phase?
Do you start with the known supplied voltage and do the calculation for each section separately, use the calculated voltage result from the previous calc for next section?
Here is a scenario; These numbers are made up, but is the method correct?
600V Supply, 50A Load
100' of 3C #4 AWG Aluminum, 600V * 0.5% = 597V
250' of 3x1C #6 AWG Copper, 597V * 0.7% = 592V
400' of 2x3C #2 AWG Aluminum 592V * 0.2% = 590V
Therefore the final voltage at the load is 590V