I have a factory motor of 710kW at 6.6Kv. A VFD will be installed, but I already have a SEL 710 relay above. Would you like to know that only the 50/51 functions are enough for VFD protection?
This is probably included under the 50/51 umbrella but depending on how your system is grounded you might still set a 50G or an 51G element to trip for ground faults on the motor circuit conductors to the VFD.