I am analyzing the relief valve protection on a vessel, and would like to have your opinion about considering overpressure by overfilling as a credible scenario.
A terminal has an ASME horizontal vessel that receives propane through a pipeline, and normally there are no operators on site. The operation is controlled from a remote location. The vessel has an electrical operated valve that isolates it from the pipeline.
The propane level is monitored using a level transmitter, preset to close the valve when HHL is reached. A level switch is installed on the vessel also set to close the valve at HHL.
a) If the terminal loses power, the valve won’t be able to close. However, the control center would notice the power lose and stop pumping: Assuming that manually stop pumping will avoid overfilling the vessel, would this still be a credible scenario for overfilling causing overpressure due to a possible operational error?
b) Would the situation change under the following scenarios?
- Permanent personnel in the Terminal, and operational procedure to manually close the valve in case of power loss.
- Providing automatic shutdown of pump if power loss (or communication loss) is detected at the control center.
- Emergency power supply in the Terminal
I will appreciate any opinion on this.
A terminal has an ASME horizontal vessel that receives propane through a pipeline, and normally there are no operators on site. The operation is controlled from a remote location. The vessel has an electrical operated valve that isolates it from the pipeline.
The propane level is monitored using a level transmitter, preset to close the valve when HHL is reached. A level switch is installed on the vessel also set to close the valve at HHL.
a) If the terminal loses power, the valve won’t be able to close. However, the control center would notice the power lose and stop pumping: Assuming that manually stop pumping will avoid overfilling the vessel, would this still be a credible scenario for overfilling causing overpressure due to a possible operational error?
b) Would the situation change under the following scenarios?
- Permanent personnel in the Terminal, and operational procedure to manually close the valve in case of power loss.
- Providing automatic shutdown of pump if power loss (or communication loss) is detected at the control center.
- Emergency power supply in the Terminal
I will appreciate any opinion on this.