Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Vertical reinforcement 1

Status
Not open for further replies.

rbhall

Civil/Environmental
Joined
Nov 24, 2011
Messages
21
Location
US
Drawings show a 12" thick concrete wall indicating double #5 at 12"oc. The contractor installed the inside #5 bars offset from the outside #5 bars. I have always been taught to install the bars directly across from each other. The drawing does not have a top view of the wall therefore I have no way to verify if the bars are required to be directly across from each other. Does anyone know of a requirement for having the bars directly across from each other?
 
There is no requirement for alignment in walls like you state.

 
It is actually a better arrangement considering clearances for concrete placement in thinner walls.

Mike McCann
MMC Engineering

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top