Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

VAV CALIBRATION DURATION

Status
Not open for further replies.

Kasim u tab

Mechanical
Joined
Sep 16, 2021
Messages
1
Location
QA
Dear engineers
Site is under construction we are doing VAV Calibration now .after calibration how many days later need to do validation of these vas’s

Regards thanks
 
You mean you calibrated the airflow station in VAV terminals?
Really depends on the type.....

I use the Accutrol VAV terminals and they have vortex-flowstations and they don't have to be field-calibrated or re-calibrated. Many use pitot-tubes. Those get dirty over time (or damaged etc.) and will drift off. They also use pressure sensors that will drift over time. Probably wouldn't hurt to verify flowrates every few years.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top