Pedarrin:
I'm suspecting the engineer of record has latched onto 2015 IBC Section 403.3.3 for secondary water supplies. This section was revised and the issue is it's not correlated to the NFPA 20 and NFPA 14 requirements for tall buildings. Section 403.3.3 states:
2015 IBC Section 403.3.3 said:
An automatic secondary on-site water supply having a capacity not less than the hydraulically calculated sprinkler demand, including the hose stream requirement, shall be provided for highrise buildings assigned to Seismic Design Category C, D, E or F as determined by Section 1613. An additional fire pump shall not be required for the secondary water supply unless needed to provide the minimum design intake pressure at the suction side of the fire pump supplying the automatic sprinkler system. The secondary water supply shall have a duration of not less than 30 minutes.
The second sentence is always applicable. The problem is all the designers read the 1st sentence and conclude that because the building is in Columbus, OH, Austin, TX or any other SDC Category A town that a secondary water supply isn't required. The fallacy is that 2015 IBC Section 403. requires the sprinkler system to comply with IBC Section 903.3.1.1 which requires the system to be
approved, which in my jurisdiction is me or my counterparts.
My jurisdiction adopted the 2015 IBC last year and we're dealing with this on a 72 story mixed occupancy Group B/R/S-1 high rise. When we adopt a new building and fire code we update NFPA 13, NFPA 14, NFPA 20 and other commonly employed NFPA standards to the latest editions. The requirements in NFPA 20 were recently revised but even if you employ an older edition, a secondary water supply is required by NFPA 14 and NFPA 20.
NFPA 14 (2016 ed) Section 7.9.3 states:
7.9.3* For buildings with two or more zones in which any portion of the higher zones cannot be supplied by means of fire department pumpers through a fire department connection, an auxiliary means of supply in the form of high-level water storage with additional pumping equipment or other means acceptable to the AHJ shall be provided.
Herein lies the issue: these tall buildings are beyond the pumping capability of the fire department. As a result, a secondary water supply is required. For the mobile pumping apparatus (a.k.a, Engine or Quint in my town) we can supply 100 PSIG to the Class I standpipe hose valve that's about 32-35 stories above the lowest level of FD access. After that, centrifugal pumps are incapable of moving water while operating within the pressure limits of the pipe, valves and fittings.
It get's even more fun when you review Section 5.6 of NFPA 20 (2013 edition) because it requires the designer to base the design on the pumping capability of the responding fire department:
5.6.2 Fire Pump Backup. Fire pumps serving zones that are partially or wholly beyond the pumping capability of the fire department apparatus shall be provided with one of the following:
(1) A fully independent and automatic backup fire pump unit(s) arranged so that all zones can be maintained in full service with any one pump out of service.
(2) An auxiliary means that is capable of providing the full fire protection demand and that is acceptable to the authority having jurisdiction.
Obviously this brings up other issues like the dead load of the static water tank and the additional electric power demand on the emergency generator because it's required to carry the Emergency power load of 2 fire pumps. However, the client is bringing the hazard to someone's town and the local FD only has so much pumping capacity and the mathematics of centrifugal pump affinity laws necessitate these additional features to the firefighters and occupants.
I hope this helps to clarify the issues and how the cited 2015 IBC provision doesn't "connect the dots" back to NFPA 14 and NFPA 20.