hello,
I'm working on performing a short circuit study in order to get the arc flash hazards. The utility servicing the customer will only provide a range of fault currents available but refuses to provide the X/R ratios.
This is what I received from the utility person I've been dealing with: (the utility's name has been replaced with XXXX)
___________________________________________________________
The following are directions I received from our corporate office:
The X/R ratios will not be provided
In order to assess the arc flash exposure both the fault current and clearing time are required to determine the level of protection needed. Instinctively it is easy to assume that the highest fault duty will provide the highest arc flash exposure but more often than not this is not true. For lower fault duties the clearing time can be quite large leading to a high calorie level. XXXX’s distribution system is very dynamic. The following factors can affect the fault duty:
1. Dependant on which circuit is supplying the transformer. XXXX’s system is dynamic and is continually being reconfigured. This can significantly change the fault duty level.
2. Transformer size (including any future replacement size)
3. Impedance of transformer (XXXX specifies a maximum and minimum impedance range)
4. Secondary impedance
The following factors can affect the fault clearing time:
1. Which protective device operates.
2. The transformer fuses may vary as there is more than one type and size that may be used.
3. The impedance of the fault.
Due to the many variables we are in the process of developing a generic table. Depending on the size and type of transformer a minimum and maximum fault current will be provided. The fault current will be calculated using the following assumptions:
1. For the minimum fault level:
Lowest system fault duty (i.e. 370A).
Use the maximum impedance for the smallest transformer able to be installed at that location.
2. For the maximum fault level:
100MVA system bus
Use the minimum impedance for the largest transformer able to be installed at that location.
Additionally it will be recommended that the customer use their own protective device to determine the fault clearing time.
____________________________________________________________
I believe I can not perform the required studies without the X/R ratio and the utility is preventing my client from providing a safe workplace in accordance with OSHA standards.
Any ideas on how to proceed from this point would be greatly appreciated.
I'm working on performing a short circuit study in order to get the arc flash hazards. The utility servicing the customer will only provide a range of fault currents available but refuses to provide the X/R ratios.
This is what I received from the utility person I've been dealing with: (the utility's name has been replaced with XXXX)
___________________________________________________________
The following are directions I received from our corporate office:
The X/R ratios will not be provided
In order to assess the arc flash exposure both the fault current and clearing time are required to determine the level of protection needed. Instinctively it is easy to assume that the highest fault duty will provide the highest arc flash exposure but more often than not this is not true. For lower fault duties the clearing time can be quite large leading to a high calorie level. XXXX’s distribution system is very dynamic. The following factors can affect the fault duty:
1. Dependant on which circuit is supplying the transformer. XXXX’s system is dynamic and is continually being reconfigured. This can significantly change the fault duty level.
2. Transformer size (including any future replacement size)
3. Impedance of transformer (XXXX specifies a maximum and minimum impedance range)
4. Secondary impedance
The following factors can affect the fault clearing time:
1. Which protective device operates.
2. The transformer fuses may vary as there is more than one type and size that may be used.
3. The impedance of the fault.
Due to the many variables we are in the process of developing a generic table. Depending on the size and type of transformer a minimum and maximum fault current will be provided. The fault current will be calculated using the following assumptions:
1. For the minimum fault level:
Lowest system fault duty (i.e. 370A).
Use the maximum impedance for the smallest transformer able to be installed at that location.
2. For the maximum fault level:
100MVA system bus
Use the minimum impedance for the largest transformer able to be installed at that location.
Additionally it will be recommended that the customer use their own protective device to determine the fault clearing time.
____________________________________________________________
I believe I can not perform the required studies without the X/R ratio and the utility is preventing my client from providing a safe workplace in accordance with OSHA standards.
Any ideas on how to proceed from this point would be greatly appreciated.