Used Fittings

Status
Not open for further replies.

Ehendrix

Mechanical
Joined
Nov 23, 2015
Messages
63
Location
US
Is there any code in NFPA 13 about reusing threaded fittings for a system that we had to turn around and modify per changes to the contract drawings??

Thanks,

Eric Hendrix, SET
NICET Certified
Design Manager
 
No sir.

Only new requirement is for sprinklers.

Chapter 6 even allows reconditioned valves and such in existing systems.

R/
Matt
 
Depending on if you are in an IBC/IFC community, the IBC/IFC has language addressing reuse of materials and equipment. 2009 IFC Section 104.7.1. Now being it is a fitting, I don't think there would be much resistance from this section. But just throwing it out there.
 