I have come across many earth fault protection arrangements, where the shunt trip of the MCCB along with an earth fault relay is used to isolate a circuit with earth fault. This arrangement is not fail safe for the following,
1) Power supply for the micro relay / earth fault / shunt trip is obatained through a fuse. Opening of the fuse will will not be noticeable, but earth fault protection is out of operation.
2) Failure of the shunt trip will also lead to the same situation.
Is there a better way of interfacing the earth fault relay for fail safe operation?