you are mixing and matching
delayed egress:: normally is a panic bar that has delayed exit
1008.1.8.6 De layed egress locks. Approved, listed, de -
layed egress locks shall be permit ted to be installed on
doors serving any occupancy except Group A, E and H
occupancies in buildings that are equipped through out
with an automatic sprinkler system in accor dance with
Section 903.3.1.1 or an approved automatic smoke or
heat detection system installed in accordance with Sec -
tion 907, provided that the doors unlock in accordance
with Items 1 through 6 be low. A building occupant shall
not be required to pass through more than one door
equipped with a delayed egress lock be fore en ter ing an
exit.
1. The doors unlock upon actuation of the automatic
sprinkler system or automatic fire detection system.
2. The doors unlock upon loss of power controlling
the lock or lock mechanism.
3. The door locks shall have the capability of being
unlocked by a signal from the fire command center.
4. The initiation of an irreversible process which will
release the latch in not more than 15 seconds when
a force of not more than 15 pounds (67 N) is ap -
plied for 1 sec ond to the release device. Initiation
of the ir reversible process shall activate an audible
signal in the vicinity of the door. Once the door
lock has been re leased by the appli ca tion of force
to the re leasing device, relocking shall be by man -
ual means only.
Exception: Where approved, a delay of not
more than 30 seconds is permit ted.
5. A sign shall be provide on the door located above
and within 12 inches (305 mm) of the re lease de -
vice read ing: PUSH UN TIL ALARM SOUNDS.
DOOR CAN BE OPENED IN 15 [30] SEC ONDS.
6. Emergency lighting shall be pro vided at the door.
or you can do a electric touch bar and mag lock which when you touch the bar, the door opens right than
If a door is required to have panic hardware to begin with thatn it must have panic hardware or equal.
not sure if this answers your questio, if not restate