UR T60 differential mis-operated on an external downstream fault. I looked into the relay settings and found several things I thought may cause the T60 mis-operated from most likely to least likely in the following order:
1) SRC 1 doesn't get any frequency and phasor measurement
2) in transformer winding settings, "Not within Zone" for both winding 1 & 2 of a Wye/Ground-Wye transformer, which I think should be set to "Not Within Zone" for Winding 1 and "Within Zone" for Winding 2
3) Reference CT was assigned wrong winding, but I don't think it will affect the differential for a fault at 4 kilometer away downstream. It may affect the relay calculation if any CT saturates.
4) transformer rating was input as ONAF rating instead of ONAN rating
Are the above findings hole the statement true? Any other settings can also cause T60 mis-operation?
Thanks in advance!