I am designing a platform stair system and for one of the load case, I am facing a strong uplift on one of the posts. We can't use a counterweight. Is there a way I can get rid of that uplift.
One way is to span a beam in the direction of a platform and create a positive connection. But then should that beam be designed for the uplift loads?
I have attached output results of the staad. Please let me know what you think about it and any suggestions would be appreciated.
Thanks.
 https://files.engineering.com/getfile.aspx?folder=10fc0d07-0db4-4f31-9b91-8f3978b595de&file=uplift.PNG
Unless I'm missing something 124# is not a lot of uplift. Can you cast the leg into a cubic foot of concrete?
Dik
We have uplift of like 650#. It's right next to the 124# post and unfortunately we can't use concrete.
The base must be anchored to something, can you justify engaging any weight of the supporting structure?
Where is the uplift coming from? I assume this is a free-standing stair and the uplift is coming from a lateral load applied at the top. Can you brace the stair to something else and eliminate the uplift?
All else fails, make sure your column is at least 650 lbs.
If you can't use concrete, then what kind of foundation are you using? What are the post bases secured to?