Hello,
We have a unit connected generator.
The generator is 11kV, 9MVA and is medium impedance grounded (25 ohms).(high impdedance would have probably been better)
The generator is connected to 2 step up transformers of 5 MVA connected in paralell.
Both transformers are exactly the same and the manufacturer has guaranteed that they can operate in paralell.
This configuration is unusual but the delivery time for 2 transformers of 5MVA was shorter than for one of 10 MVA.
The WYE side are 11kV and connected to the generator.
The DELTAS side are 15.4kv and ungrounded.
There is one voltage transformer (15.4kv/V3 / 110/V3) on each phase on the 15.4kV side connected between phase and ground.
When we started the generator, one protection relay connected on the 15.4kV gave an alarm indicating that the zero sequence voltage is too high.
The voltage measured were (see attached document)
- VAN = 9.375 kV at 0°
- VBN = 9.224 kv at 248.1°
- VCN = 8.154 kv at 123.0°
The calculated zero sequence voltage was 2.272 kV.
We thought there was an insulation failure causing a phase to ground fault on the 15.4kV.
But the isolation test with a megger showed a good insulation (2.8Gohms) between phase to ground.
The transformer manufacturer told us that the relay was set too sensitive (3V0 = 10V secondary = 1400 Vprimary) and that the relay readings should not be taken into account as the DELTA is ungrounded.
According to them the problem will disappear once the unit is synchronized.
Have you ever seen this problem?
Could the problem come from the fact that the transformers are in paralell?
We have a smaller generator with the same configuration except that there is only one 5MVA step up transformer and there is no problem with it.
Thanks for your help,
We have a unit connected generator.
The generator is 11kV, 9MVA and is medium impedance grounded (25 ohms).(high impdedance would have probably been better)
The generator is connected to 2 step up transformers of 5 MVA connected in paralell.
Both transformers are exactly the same and the manufacturer has guaranteed that they can operate in paralell.
This configuration is unusual but the delivery time for 2 transformers of 5MVA was shorter than for one of 10 MVA.
The WYE side are 11kV and connected to the generator.
The DELTAS side are 15.4kv and ungrounded.
There is one voltage transformer (15.4kv/V3 / 110/V3) on each phase on the 15.4kV side connected between phase and ground.
When we started the generator, one protection relay connected on the 15.4kV gave an alarm indicating that the zero sequence voltage is too high.
The voltage measured were (see attached document)
- VAN = 9.375 kV at 0°
- VBN = 9.224 kv at 248.1°
- VCN = 8.154 kv at 123.0°
The calculated zero sequence voltage was 2.272 kV.
We thought there was an insulation failure causing a phase to ground fault on the 15.4kV.
But the isolation test with a megger showed a good insulation (2.8Gohms) between phase to ground.
The transformer manufacturer told us that the relay was set too sensitive (3V0 = 10V secondary = 1400 Vprimary) and that the relay readings should not be taken into account as the DELTA is ungrounded.
According to them the problem will disappear once the unit is synchronized.
Have you ever seen this problem?
Could the problem come from the fact that the transformers are in paralell?
We have a smaller generator with the same configuration except that there is only one 5MVA step up transformer and there is no problem with it.
Thanks for your help,