I found a few threads on this but nothing that exactly answered my question. I'm reviewing a design for a CMU building with an untopped precast plank roof.
See the sketch below for a representative diagram.
I often see documents (like the PCI manual) talk about using friction in the joints between the panels to create a 'contiguous' diaphgram when you don't have a topping. I don't understand how this works when you have suction on the walls.
The top of the south wall in my diagram is only connected to the south-most panel. As wind "sucks" it south, it will pull that edge panel away from the remaining panels unless some kind of positive connection is provided between every panel (grouted U-bar, weld plate, etc.). How is it that any situation can rely on friction when you always have a potential suction?
See the sketch below for a representative diagram.
I often see documents (like the PCI manual) talk about using friction in the joints between the panels to create a 'contiguous' diaphgram when you don't have a topping. I don't understand how this works when you have suction on the walls.
The top of the south wall in my diagram is only connected to the south-most panel. As wind "sucks" it south, it will pull that edge panel away from the remaining panels unless some kind of positive connection is provided between every panel (grouted U-bar, weld plate, etc.). How is it that any situation can rely on friction when you always have a potential suction?