Underground Firewater pipe-No Cement lining

Status
Not open for further replies.

movasra

Structural
Nov 15, 2007
23
Hello,

We have a situation that the contractor has installed an underground carbon steel fire water pipe that goes to a hydrant. The pipe is wrapped but it is not cement lined. I am trying to find any statement in AWWA standards (C205 maybe) that approves the pipe material.

I have already purchased AWWA C200 , C604 and NFPA 24. I couldn’t find anything in C200 and C604.
NFPA 24 allows using CS without cement lining as long as it’s internally galvanized.

Any advice would be appreciated.
 
Replies continue below

Recommended for you

A contractor I work with, has seen carbon steel piping used as fire water supply piping at a facilty near here.
The lines were installed in the late 80's and had to be replaced 2006-2008 time frame. They had actually holed through.
The reason I know about it is he could not come to my job because they were busy digging up that mess. But they did get 20+ years out of the pipe.
He did not mention the schedule. Size was 10 or 12 inch.

Regards
StoneCold
 
What does your specification require?

ANSI/AWWA C200 is the standard for steel pipe.




I don't think a lining is required by C200, but most specifiers will require a lining or coating of some sort.
 