- Nov 13, 2009
- 35
I need to run underground cabling from my battery bank to my inverters. My inverters are rated for 6000VA and are 93.5% efficient, so I have calculated that the DC current will be 134A at 48Vdc. I have 2 inverters, but I plan to parallel the battery cables which, if I read the NEC correctly, I am allowed to do with 1/0 or larger wire. If I read further on, figure 310.60 details the required spacing for underground cabling, but this appears to be applied to 2001V-35,000V rated cables. Is there a horizontal spacing requirement for low voltage cables? The cables will be in 2 separate conduits, 2 wires to a conduit, if that makes a difference. The only thing I can find is 310.15(B)(3)(b) which states, “Spacing between conduits, tubing, or raceways shall be maintained.”
I’m also wondering how to determine the ambient temperature. I know that the cables need to be buried at least 18 inches below grade. What ambient temperature should I use as an adjustment factor? Air temperatures here, in the summer, typically reach 110F. Obviously, the temperature 18 inches below grade will be something lower than that. Do I need to measure the temperature of the soil at that depth? Or is there a thumbrule that can be applied? I’m thinking that the safest thing to do would be to use peak ambient air temperature. For this installation, it will not affect the cable size because a 110F correction factor puts me at a 1/0 cable; any lower ambient temperature would reduce my required cable size, but I would still need to use 1/0 in order to parallel them legally. However, I would like to know for future reference.
I’m also wondering how to determine the ambient temperature. I know that the cables need to be buried at least 18 inches below grade. What ambient temperature should I use as an adjustment factor? Air temperatures here, in the summer, typically reach 110F. Obviously, the temperature 18 inches below grade will be something lower than that. Do I need to measure the temperature of the soil at that depth? Or is there a thumbrule that can be applied? I’m thinking that the safest thing to do would be to use peak ambient air temperature. For this installation, it will not affect the cable size because a 110F correction factor puts me at a 1/0 cable; any lower ambient temperature would reduce my required cable size, but I would still need to use 1/0 in order to parallel them legally. However, I would like to know for future reference.