Under Frequency Load shedding

Status
Not open for further replies.

Riandika13

Electrical
Sep 15, 2022
1
Hi I have a question regarding load shedding in power systems, why do most load shedding use frequency as a parameter? Frequency changes due to load unbalance, so why not use load parameters for load shedding determination?
 
Replies continue below

Recommended for you

Load shedding uses multiple parameters, of which frequency is one. As Greg mentioned, actual load values are few and far between when initially setting up a load shed scheme. However, certain large-scale (% of max load) changes are known to disrupt system stability and can thus be coded into the scheme from the outset (for example, a 50% step in total load vs current spinning reserve). Smaller changes will cause frequency perturbations that can be picked up through normal system monitoring.