Unbalanced Snow Load IBC 2000 2
cmrazik
I am designing roof rafters for a single family residence. If I apply an unbalanced snow load, the rafters in the IBC Residential Code tables do not work. (My model includes a ceiling joist). I can only get the rafters in the table to work with balanced snow loads.
Does anybody know of a stipulation in the Code where you do not have to apply unbalanced snow loads to residential buildings?
Thanks!
So why dont you design with an unbalanced snow load.
I don't want to design the roof for unbalanced snow load if I don't have to. I was already accused by another engineer of being overconservative with the roof design on a previous residential design project. I would like to know definatively either way.
The leeward drifts from the ASCE 7 hammer a rafter design with 150% Pf. As I understand it, this is what the IBC says to do irrespective of occupany (I=1.0).
You are governed by the IRC. The IBC is a code book whereas I view the IRC as more of a recipe book. I am doing good to stay up with the IBC changes every three years and thus do not profess to know that much about the IRC. Look in the IRC and I expect it says the span tables are OK w/o drifting. IRC R301.2.3.
For what it's worth, I design any rafter and its connections for the drifted snow condition.
Check whether IBC and ASCE 7 even govern this design. Usually, the IRC controls residential design and you may not have to even refer to the other two.
If it is single family with 3 stories or less, then IRC is your code. If your ground snow load is 70 psf or less, you use the tables in IRC (chap 5,6 and 8). I don't have the commentary handy, but I think your issue is taken into account in the table values.
ZCP