Can someone tell me what a typical amount, percent of nameplate, that a 3 phase 480VAC, induction(Squirrel cage) motor might be?
I have a 20hp motor that when disconnected from the load, draws about 20amps just running. The amps are measured at the leads to the motor with a clip-on ammeter. The amps were measured about 20 seconds after starting. The voltages were normal and held steady. The shaft is not bound and the rotor slowly spins down after the power is shut off. The motor does not overheat. We checked the no-load current because we felt the full-load was close to the nameplate. We have four of these motors all acting the same. They were rewound about 5 years ago.
This seems like an awful lot of amps for speed no-load.
The motor draws about 28amps when connected to the load.
I have a 20hp motor that when disconnected from the load, draws about 20amps just running. The amps are measured at the leads to the motor with a clip-on ammeter. The amps were measured about 20 seconds after starting. The voltages were normal and held steady. The shaft is not bound and the rotor slowly spins down after the power is shut off. The motor does not overheat. We checked the no-load current because we felt the full-load was close to the nameplate. We have four of these motors all acting the same. They were rewound about 5 years ago.
This seems like an awful lot of amps for speed no-load.
The motor draws about 28amps when connected to the load.