The ratio: low speed HP / hi speed HP is usually 1:2, for the majority of two-speed Dahlander motors with constant torque winding. However, there are many such motors where the ratio is 1: 1.5. Are the internal connection diagrams and wiring the same in both cases or they are different? Does anyone have an example?
Zlatkodo
 
Replies continue below

Recommended for you

Hi, Electricpete,
I know what is the PAM winding, but my question is not about the PAM windings than about the two speed, constant torque , Dahlander windings with speed ratio 1:2 .
Zlatkodo
 
The Dahlanders seem to be constant torque 2Y/1Y connections. They would be the same connections for a 1:2 or a 1:1.5 hp ratio. The only reason they derate the 1:2 is to maintain a decent flux.
 
Sorry, I misunderstood your question.

=====================================
(2B)+(2B)' ?
 
Hi, Motorwinder,
Probably, you thought:
"The Dahlanders seem to be constant torque 2Y/D connections."
Zlatkodo
 
Hi, Starkopete,
You talk about the difference between constant torque and variable torque, but my question relates only to constant torque, ie question is: is the internal connection diagram the same for both cases:
- the two-speed Dahlander constant torque, D/YY winding with HP ratio 1: 2,
- the two-speed Dahlander constant torque, D/YY winding with HP ratio 1: 1,5
Zlatkodo
 
Hi Zlatkodo,
Now I'm really going to confuse things. From a WEG motor catalog in reference to Dahlander two speed motors:

"Constant torque:
Torque is constant on both speeds and rated power ratio is 0.63:1 In this case, motor has a D/YY connection.
Example: 0.63/1HP motor – IV/II pole - D/YY.
This connection is suitable for applications where the load torque curve remains constant with the speed variation."

The .63:1 power ratio can be re-written as 1:1.58, if it is truly a "constant torque" connection you'd expect a 1:2 power ratio. Any one have any ideas.

Thanks

 
Hi,
I checked with one of EASA's Engineers and he gave me the following reply:

"NEMA uses an artificially simple 2:1 or constant torque, and 4:1 for variable torque, where the IEC motors use the actual torque / KW ratio instead."

Based on that reply the answer to your OP would be yes, the internal connection diagrams and wiring are the same.

Thanks


 
Maybe this is over simplifying but if both motors are D/YY connected then both would connect the same.

I would also agree that the statement that the typically quoted 2:1 or 1:1 HP ratio is a simplification and many motors do not actually have a 2:1 or 1:1 HP ratio.
 