I am using a TVS to protect an SSR (no zero cross circuitry) from a soleniod valve. The specifications of the three parts in question are:
SSR: 2A continous - 100 V max
TVS: (SMBJ51CA) Bi-directional - 82 V max clamp - 7.3 A max peak pulse current
Solenoid: 1.1 A max continous - 24 VAC
My calculation for the peak pulse power is Ppeak=Imax x Vclamp = 1.1 x 82 = 90.2 W
The maximum time for the inductive kickback transient is 1ms and soleniod is only turned on every 1 minute or so. The average power dissipated by the TVS is 90.2 x .001 / 60 = 0.0015Wavg. This tells me that all is well since the continous power dissipation of such a part is well into the 1W area.
Am I in the clear here? Or did I miss something?
Thanks
X-) [sig][/sig]