Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

tubular recuperator

Status
Not open for further replies.

HSadeghian

Mechanical
Joined
Aug 2, 2007
Messages
3
Location
IR
Under which code/standard the tubular recuperators are designed?
 
HSadeghian,

By recuperator, I presume that you are referring to a tubular air-to-air or gas-to-air exchanger operating at essentially atmospheric pressure on both sides.

If that is the case, there are no specific industry standards that I am aware of that would apply. Basically, such an exchanger would be designed per the project specifications, which need to be custom taylored to the specific application. Here are a few points to consider in writing the spec:

1. Materials of construction for all major components.
2. Insulation (if any) - type, thickness, lagging, etc.
3. Obvious performance specs, including maximum allowable pressure drops on both sides (very important). Include operating pressures of both fluids.
4. Provisions for differential thermal expansion.
5. Some definition of the importance (or lack thereof) of leakage from the higher pressure side to the lower pressure side. In some applications itis very important to have no leakage. In others, some leakage is OK.

Regards,

Speco (
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top