chuckd83
Electrical
- Oct 2, 2014
- 43
On a 138/25 kV, Dyn1 transformer test report, I'm given
Test = LV - HV open
MVA = 43.0
%Z0 = 8.11%
Ohms = 0.393
Is there a way to calculate the zero sequence X/R from this?
Edit: I think the %Z0 and ohms are saying the same thing.
Zbase = (25/sqrt(3))^2 / 43 = 4.845 ohms
Zpu = 0.393 / 4.845 = 0.0811
I thought the 0.393 may be the R, but I guess not.
Test = LV - HV open
MVA = 43.0
%Z0 = 8.11%
Ohms = 0.393
Is there a way to calculate the zero sequence X/R from this?
Edit: I think the %Z0 and ohms are saying the same thing.
Zbase = (25/sqrt(3))^2 / 43 = 4.845 ohms
Zpu = 0.393 / 4.845 = 0.0811
I thought the 0.393 may be the R, but I guess not.
Last edited: