rockman7892
Electrical
- Apr 7, 2008
- 1,178
We have a utility 230kV Delta/4.16kV Wye 15MVA transformer which serves our plant. The secondary wye is LRG at 400A, so therefore we have no loads which are connected line-nuetral on this transformer, and I would therefore not expect to see any nuetral current.
We have recently just added an identical second transformer onto the same utility feed, and it is also LRG at 400A and tied into the same grouding system.
Since it is tied into the same grounding system you are saying there is the possibility to have nuetral current existing on one or both of these transformers?
We have recently just added an identical second transformer onto the same utility feed, and it is also LRG at 400A and tied into the same grouding system.
Since it is tied into the same grounding system you are saying there is the possibility to have nuetral current existing on one or both of these transformers?