Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer impedance calculation

Status
Not open for further replies.

LaliGuras

Electrical
Nov 11, 2005
7
How do i calculate X and R for a power transformer like 10 or 20 MVA if i have only Z. Is there any standard X/R ratios for these transformers?
 
Replies continue below

Recommended for you

Cutler Hammer list transformers 10 mva 69kv as
5.5% x/r = 10 above 69kv 7.5% x/r = 12

12 mva to 30 mva 10% x/r =20
 
The IEEE Red Book has a graph of average X/R ratio as a function of transformer type and rating.

There is no way to directly calculate without the transformer test data.
 